• Кондей врв хайсенс Модель AVWT-154U6SS коды ошибок 5 0 5 1

Кондей врв хайсенс Модель AVWT-154U6SS коды ошибок

Автор сега, 08 сентября 2017, 22:33:24

« назад - далее »

0 Пользователи и 1 гость просматривают эту тему.

сега

Ребята помогите или подскажите где можно скачать коды ошибок и сервиз мануалы на китайца хайсенс врв.спасибо.

Ремонт кондиционеров

сега


wartandax

Вот коды ошибок


сега

Все поможет лишним не будет. Спасибо

Crazy Mont

01 Indoor Unit Activation of Protection Device (Float Switch)
Activation of Float Switch
(High Water Level in Drain Pan,
Abnormality of Drain Pipe, Float Switch or Drain Pan)
02 Outdoor Unit Activation of Protection Device
(High Pressure Cut)
Activation of PSH (Pipe Clogging, Excessive
Refrigerant, Inert Gas Mixing)
03
Transmission
Abnormality between Indoor and Outdoor
Incorrect Wiring, Loose Terminals, Disconnect Wire,
Blowout of Fuse, Outdoor Unit Power OFF
04
04.
Abnormality between Inverter PCB and Outdoor PCB
Abnormality between Fan Controller and Outdoor PCB
Inverter PCB - Outdoor PCB Transmission Failure
(Loose Connector, Wire Breaking, Blowout of Fuse)
(Loose Connector, Wire Breaking, Blowout of Fuse)
Fan Controller - Outdoor PCB Transmission Failure
05 Supply Phase Abnormality Power Source Phases Incorrect Power Source, Connection to
Reversed Phase, Open-Phase
06
Voltage
Abnormal Inverter Voltage Outdoor Voltage Drop, Insufficient Power Capacity
06. Abnormal Fan Controller Voltage Outdoor Voltage Drop, Insufficient Power Capacity
07
Cycle
Decrease in Discharge Gas Superheat
Excessive Refrigerant Charge, Failure of Thermistor,
Incorrect Wiring, Incorrect Piping Connection,
Expansion Valve Locking at Opened Position
(Disconnect Connector)
08 Increase in Discharge Gas Temperature
Insufficient Refrigerant Charge, Pipe Clogging,
Failure of Thermistor, Incorrect Wiring,
Incorrect Piping Connection, Expansion Valve Locking
at Closed Position (Disconnect Connector)
0A Transmission Abnormality between Outdoor and Outdoor Incorrect Wiring, Breaking Wire, Loose Terminals
0b
Outdoor Unit
Incorrect Outdoor Unit Address Setting Duplication of Address Setting for Outdoor Units
(Sub Units) in Same Refrigerant Cycle System
0C Incorrect Outdoor Unit Main Unit Setting Two (or more) Outdoor Units Set as "Main Unit"
Exist in Same Refrigerant Cycle System
11
Sensor on
Indoor Unit
Inlet Air Thermistor
Incorrect Wiring, Disconnecting Wiring
Breaking Wire, Short Circuit
Incorrect Wiring, Disconnecting Wiring
Breaking Wire, Short Circuit
12 Outlet Air Thermistor
13 Freeze Protection Thermistor
14 Gas Piping Thermistor
19 Fan Motor Activation of Protection Device for Indoor Fan Fan Motor Overheat, Locking
21
Sensor on
Outdoor Unit
High Pressure Sensor
22 Outdoor Air Thermistor
23 Discharge Gas Thermistor on Top of Compressor
24 Heat Exchanger Liquid Pipe Thermistor
25 Heat Exchanger Gas Pipe Thermistor
29 Low Pressure Sensor

31
System
Incorrect Capacity Setting of Outdoor Unit and
Indoor Unit
Incorrect Capacity Code Setting of Combination
Excessive or Insufficient Indoor Unit Total
Capacity Code
35 Incorrect Setting of Indoor Unit No. Duplication of Indoor Unit No. in same Ref. Gr.
36 Incorrect of Indoor Unit Combination Indoor Unit is Designed for R22
38
Abnormality of Picking up Circuit for Protection
in Outdoor Unit
Failure of Protection Detecting Device
(Incorrect Wiring of Outdoor PCB)
39 Compressor
Abnormality Running Current at
Constant Speed Compressor
Overcurrent, Blowout Fuse, Current Sensor Failure,
Instantaneous Power Failure, Voltage Drop,
Abnormal Power Supply
3A
Outdoor Unit
Abnormality of Outdoor Unit Capacity Outdoor Unit Capacity > 1350KBtu/h
3b Incorrect Setting of Outdoor Unit Models
Combination or Voltage
Incorrect Setting of Main and Sub Unit(s)
Combination or Voltage
3d Abnormality Transmission between Main Unit
and Sub Unit(s)
Incorrect Wiring, Disconnect Wire, Breaking Wire,
PCB Failure
43
Protection
Device
Activation of Low Pressure Decrease Protection
Device
Defective Compression (Failure of Compressor
of Inverter, Loose Power Supply Connection)
44
Activation of Low Pressure Increase Protection
Device
Overload at Cooling, High Temperature at Heating,
Expansion Valve Locking (Loose Connector)
45
Activation of High Pressure Increase Protection
Device
Overload Operation (Clogging, Short-Pass), Pipe
Clogging, Excessive Refrigerant, Inert Gas Mixing
47
Activation of Low Pressure Decrease Protection
Device (Vacuum Operation Protection)
Insufficient Refrigerant, Refrigerant Piping, Clogging,
Expansion Valve Locking at Open Position (Loose Connector)
48 Activation of Inverter Overcurrent Protection Device Overload Operation, Compressor Failure
51 Sensor Abnormal Inverter Current Sensor Current Sensor Failure
53
Inverter
Inverter Error Signal Detection Driver IC Error Signal Detection (Protection for
Overcurrent, Low Voltage, Short Circuit)
54 Abnormality of Inverter Fin Temperature Abnormal Inverter Fin Thermistor,
Heat Exchanger Clogging, Fan Motor Failure
55 Inverter Failure Inverter PCB Failure
57
Fan
Controller
Activation of Fan Controller Protection
Driver IC Error Signal Detection (Protection for Overcurrent,
Low Voltage, Short Circuit), Instantaneous Overcurrent
5A Abnormality of Fan Controller Fin Temperature Fin Thermistor Failure, Heat Exchanger Clogging,
Fan Motor Failure
5b Activation of Overcurrent Protection Fan Motor Failure
5c Abnormality of Fan Controller Sensor
Failure of Current Sensor (Instantaneous Overcurrent,
Increase of Fin Temperature, Low Voltage, Earth Fault, Step-Out)
EE Compressor Compressor Protection Alarm
(It is can not be reset from remote Controller)
This alarm code appears when the following alarms*
occurs three times within 6 hours.
*02, 07, 08, 39, 43 to 45, 47
b1 Outdoor Unit
No. Setting
Incorrect Outdoor Unit Address Number
or Unit Number Setting
Over 64 Number is Set for Address or Refrigerant
Cycle.
b5 Indoor Unit
No. Setting Incorrect Indoor Unit Connection Number Setting
More than 17 Non-Corresponding to Hi-NET II
Units are Connected to One System.