Это всё уже реализовано в инвертерных моделях.
Например...
Daikin. Вот, например, цитата из сервис мануала той модели, что стоит у меня. В принципе, у всех инвертерных моделей Daikin, Mitsubisi и т. д. всё аналогично.
(1) Outdoor Heat Exchanger Thermistor
1. The outdoor heat exchanger thermistor is used for controlling the target discharge pipe
temperature. The system sets the target discharge pipe temperature according to the
outdoor and indoor heat exchanger temperature, and controls the outdoor electronic
expansion valve opening so that the target discharge pipe temperature can be obtained.
2. In cooling operation, the outdoor heat exchanger thermistor is used for detecting the
disconnection of the discharge pipe thermistor. When the discharge pipe temperature drops
below the outdoor heat exchanger temperature by more than a certain value, the discharge
pipe thermistor is judged as disconnected.
3. In cooling operation, the outdoor heat exchanger thermistor is used for high pressure
protection.
(2) Discharge Pipe Thermistor
1. The discharge pipe thermistor is used for controlling discharge pipe temperature. If the
discharge pipe temperature (used in place of the inner temperature of the compressor) rises
abnormally, the operating frequency becomes lower or the operation halts.
2. The discharge pipe thermistor is used for detecting disconnection of the discharge pipe
thermistor.
(3) Gas Pipe Thermistor
In cooling operation, the gas pipe thermistor is used for gas pipe isothermal control. The system
controls outdoor electronic expansion valve opening so that the gas pipe temperature in each
room becomes equal.
(4) Indoor Heat Exchanger Thermistor
1. The indoor heat exchanger thermistor is used for controlling the target discharge pipe
2. In cooling operation, the indoor heat exchanger thermistor is used for freeze-up protection
control. If the indoor heat exchanger temperature drops abnormally, the operating frequency
3. In cooling operation, the indoor heat exchanger thermistor is used for anti-icing function. If
any of the following conditions are met in the room where operation halts, it is assumed as
icing.
The conditions are
Tc ≤ – 1° C
Ta – Tc ≥ 10° C
where Ta is the room temperature and Tc is the indoor heat exchanger temperature.
4. In heating operation, the indoor heat exchanger thermistor is used for heating peak-cut
control. If the indoor heat exchanger temperature rises abnormally, the operating frequency
5. In heating operation, the indoor heat exchanger thermistor is used for detecting the
below the highest indoor heat exchanger temperature by more than a certain value, the
discharge pipe thermistor is judged as disconnected.
6. When only one indoor unit is operating, the indoor heat exchanger thermistor is used for
subcooling control. The actual subcool is calculated with the liquid pipe temperature and the
indoor heat exchanger temperature. The system controls the outdoor electronic expansion
valve openings to obtain the target subcool.
7. The indoor heat exchanger thermistor is used for wiring error check function. The refrigerant
flows in order from the port A to detect the indoor heat exchanger temperature one by one,
and then wiring and piping can be checked.
(5) Liquid Pipe Thermistor
1. When only one indoor unit is in heating, the liquid pipe thermistor is used for subcooling
control. The actual subcool is calculated with the liquid pipe temperature and the maximum
2. In heating operation, the liquid pipe thermistor is used for liquid pipes isothermal control. The
system controls the outdoor electronic expansion valve opening so that the liquid pipe
temperatures in each room becomes equal.